Esko said:
The shielding should, as Erik stated, be connected to REAL earth at one and ONLY one point. No, otherwise the shield makes no sense for HF! PROFIBUS connectes the shield to all involved enclosures, which all are individually connected to protection earth. A ground loop in the shield is of no danger, due to the symmetric signaling and the use of soft grounding. You won't see anything on the a-line and b-line. Esko said:
Having the signal ground running inside the mantle is also a good idea. This is the only way! To prevent common mode noise. Kai |